Thanks Dennis.
210.19(A)(3) also says branch circuit conductors shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served.
If the range is 12 kW, wouldn?t the maximum load to be served be 12 kW? This would required 12,000 / 240 = 50 A ampacity?
Thanks Dennis.
210.19(A)(3) also says branch circuit conductors shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served.
If the range is 12 kW, wouldn?t the maximum load to be served be 12 kW? This would required 12,000 / 240 = 50 A ampacity?
Range is a non continuous load so I agree with what you have there except 40 amps is the smallest allowed
Thanks Dennis.
210.19(A)(3) also says branch circuit conductors shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served.
If the range is 12 kW, wouldn?t the maximum load to be served be 12 kW? This would required 12,000 / 240 = 50 A ampacity?
The load to be served IMO is what the demand factor of T. 220.55 allows. This has been argued many times here in the [past. Ranges have thermostats that cycle on and off so the actual load is never the entire 12kw. Interestingly enough- as I said before- a 16kw range would also only require a 40 amp circuit. Now one may pause at that but that is what would be allowed by the residential table of 220.55