H hhsting Senior Member Location Glen bunie, md, us Occupation Junior plan reviewer Oct 6, 2020 #1 In dwelling unit bedroom can one branch circuit from one 15A or 20A circuit breaker feed both lights and receptacles?
In dwelling unit bedroom can one branch circuit from one 15A or 20A circuit breaker feed both lights and receptacles?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Oct 6, 2020 #2 Yes, why would you think otherwise?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Oct 7, 2020 #3 If not there would be millions of existing dwellings out of compliance. 210.23 is your reference.