Originally posted by vanwalker:
2002 230.72 c GEO
I don't see the answer to the original question in 230.72 (C).
What herndon asked was,
Are they required to have a main breaker in the load center in the apartment?
I believe that the answer is no. As long as the breaker that is protecting the individual unit feeders is not larger than the rating of the panel board it would be perfectly acceptable for them to be main lug only.
If, on the other hand, the feeders supply multiple units because individual metering is not being used then the panels would need to have a main breaker or breakers to comply with 408.16.
408.16 Overcurrent Protection.
(A) Lighting and Appliance Branch-Circuit Panelboard Individually Protected. Each lighting and appliance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard.
Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard.
I think we would all agree that the panels serving dwelling units are inevitably lighting and appliance panelboards by definition.
--
Tom