Article 310.15(A)(6) is for 120/240 volt, single phase dwelling services and feeders. The table 310.15 shows #2 aluminum for 100 amps. This section does not apply to non-dwelling units.charlie b said:Where did you get the notion that the code "requires" #2 aluminum? The NEC certainly does not. What is the nature of the existing installation or the new project you are discussing?
Wow I agree pismo. Nice to see you again.pismo said:Article 310.15(A)(6) is for 120/240 volt, single phase dwelling services and feeders. The table 310.15 shows #2 aluminum for 100 amps. This section does not apply to non-dwelling units.
[/quote]pismo said:The table 310.15 shows #2 aluminum for 100 amps.charlie b said:Where did you get the notion that the code "requires" #2 aluminum? The NEC certainly does not.
My point exactly. It also does not prohibit using 4/0 aluminum, though I doubt many would choose to do that. What the code "requires" is that we not use anything with a lower ampacity, unless that other thing is described as being acceptable for that application in some other applicable article or table. The code gives minimums, not absolutes.celtic said:It may "show" it, but it does not "require" it. CU would also be allowed.
Table 310.16.t wheeler said:I would like to know what table or section addresses this for a non-dwelling applications...and what size is permissable.
t wheeler said:I would like to know what table or section addresses this for a non-dwelling applications...and what size is permissable.
I would also point out that a sub-panel (meaning a "real" sub-panel, not a main-lug "main" panel fed from a remote main disconnect) also does not qualify, even residential, and #2 al is limited to 90 amps. Here's why I say that; note quoted text:pismo said:Article 310.15(A)(6) is for 120/240 volt, single phase dwelling services and feeders. The table 310.15 shows #2 aluminum for 100 amps. This section does not apply to non-dwelling units.
pismo said:The code is just a minimum. That means #2 aluminum is the minimum.
No, but #3 could.celtic said:You sure about that....couldn't #4 CU also be considered the "minimum"?![]()
LarryFine said:No, but #3 could.
310.15 says dwelling services and feeders.LarryFine said:No, but #3 could.
As above, only " the feeder conductors that serve as the main power feeder to a dwelling unit" may use table 310.15(B)(2)(a); all other uses need to use Table 310.16.
pismo said:310.15 says dwelling services and feeders.
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s). The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met.
So what you are saying is I can, for example use the #2 al. for my service entrance, then use table 310.16 for a sub-panel? This would mean from the service I would have to use 1/0 al? I read the entire section. The second to last sentence says " the feeder conductors to a dwelling unit shall not be required to be larger than the service entrance conductors." With that said, the #2 al. would be adequate for the 100 amp sub.roger said:You have to read further into 310.15(B)(6) to see that only feeders considered as Main Power Feeders as defined in the section can use the reduction, not all feeders meet this definition.
Roger
pismo said:So what you are saying is I can, for example use the #2 al. for my service entrance, then use table 310.16 for a sub-panel? [
pismo said:This would mean from the service I would have to use 1/0 al?
pismo said:I read the entire section. The second to last sentence says " the feeder conductors to a dwelling unit shall not be required to be larger than the service entrance conductors." With that said, the #2 al. would be adequate for the 100 amp sub.