FWIW, the term residence is used only 3 times, in its plural form residences, in the entire 2011 NEC. Each of those 3 times it is in an Informational Note.Is there a difference between a dwelling and a residence? as in, when hooking up a 300 amp service to 10 residences with a common area....
Thanks
I was asked a question:
As an E.I. you arrive for a final inspection of the 300 amp service. There are 10 'residences' and a common area, what do you look for?
The Q was NOT dwelling unit, guest room, or hotel. but 'residence'.
There are too many different ways the actual premises could be structured to give a simple answer.
This might be what is called a Single Room Occupancy (SRO) hotel. Each "residence" has no private bathroom or cooking facilities.
It could be group home with extra privacy.
It could be a condominium with individually owned dwelling units and common property belonging to the condo association.
It could be an apartment complex with free standing or stacked units and a common access and rec area.
(Some of those seem unlikely given the limits of a 300 amp service, but....)
As stated, there is no answer except that maybe the first thing I would look for is evidence of what it actually is!![]()
The problem is the EI's failure to use the proper terminology; start there.
240.24 Location in or on Premises.
(B) Occupancy. Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy, unless otherwise permitted in 240.24(B)(1) and (B)(2).