E/G Protection Location

Status
Not open for further replies.

Designer69

Senior Member
Is it acceptbable to have the E/G protection switchboard located in a separate room outside of the E/G enclosure, as shown on the pic?

There is a emerg. power off pushbutton outside the enclsure.

Thank You

egquestion.jpg
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, a disconnecting means is required if the conditions are not meet NEC Art.445.18:
445.18 Disconnecting Means Required for Generators.
A disconnecting means is required
except where both of the following conditions apply:
(1) The driving means for the generator can be readily shut down.

(2) The generator is not arranged to operate in parallel with another generator or other source of voltage.
Emergency generator disconnecting means.jpg
 