Is there - or was there a code for emergency illumination to be from a local lighting circuit if no seperate source is supplied? i.e. Emergency ballasts in 2x4's in an office and switched...
A correctly placed 12/3 might well work for you!....Emergency ballasts in 2x4's in an office and switched...
NEC 700.12 (F)
...the same branch circuit as that serving normal lighting in the area and connected ahead of any local switches.
how do you comply if the room's lighting is supplied through a dimmer cabinet?
Yep - thats the one - I must've gone past it a dozen times....NEC 700.12 (F)
...the same branch circuit as that serving normal lighting in the area and connected ahead of any local switches.
That is if you CAN... These today were all E-ballasts - which had to be from the same circuit as the timer/motion panel that fed them and the phase that the light in each area was on...It's still the same, it comes off the unswitched side of lighting circuit. If more than 3 circuits lighting a single area, you then CAN feed the E-lights seperately.
It's still the same, it comes off the unswitched side of lighting circuit. If more than 3 circuits lighting a single area, you then feed the E-lights seperately.
The E-lights in the unit - should be off of the unit panel. The prospective tenant has no access to the house panel, and the house panel serves no lighting in the unit. While the house panel serves more than 3 circuits of 'house' lighting - it serves no part of the floor this unit is even on, or the other two... The floor this unit is on - has a house panel with no emergency lighting at all, but serves all of the lighting on that floor in the common areas - which is how I figured this out. (Shutting of the lighting on that floor - from that panel should have had E-lights on... - instead - it was pitch black.It should be on the house panel...