I'm looking at a single phase 50 kVA, 13.8/0.24 kV transformer that is protected by a 10E fuse. The primary FLA is 3.6 A. This is a station service transformer and the fuse is its only protection.
When I plot the fuse and transformer on a TCC, it becomes obvious that the transformer damage curve is not fully protected. This is because by NEMA standard, it takes up to 5 minutes for an E-rated fuse to operate for currents 200-240% of its rating. i.e. the 10E fuse will never operate for currents less than 20 A.
Given this, I'm inclined to replace it with a 5E or 7E fuse. I'm also curious if the current installation meets the requirements of NEC Table 450.3(A) which stipulates the maximum fuse rating must be 300% FLA (10.8 A in my case). The fuse rating is 10E, or 20 - 24 A.
When I plot the fuse and transformer on a TCC, it becomes obvious that the transformer damage curve is not fully protected. This is because by NEMA standard, it takes up to 5 minutes for an E-rated fuse to operate for currents 200-240% of its rating. i.e. the 10E fuse will never operate for currents less than 20 A.