mike k
Member
- Location
- Pennsylvania
I am working on a project where the engineer designed an E-stop system to drop out all the circuits within a room of the building. The building is a military facility and used for testing & calibration of special equipment. There are several different voltages AC & DC within the space(s). Each space (room) has E-stop buttons a predetermined location around the perimeter of the room. All the circuits that enter the room are (branch circuits & Panel board feeder circuits) and controlled by mechanically held contactors. I have now way of knowing what type of equipment or the final use of this facility. This is do to the sensitive nature of the equipment which is to be installed by their personal after our scope of work has been completed. The problem I have is the E-stop circuit has a key rest (sounds good) it also has an interposing relay (good so far) which basically opens up after the E-stop has been depressed and closes (energizes) after the key reset and the relay holds itself in; but if the control circuit (voltage) is lost there the relay will open but there is no way to drop out or ?unlatch? the mechanically held contactors because of no (Voltage). Is this a proper design? What concerns should I pose to the customer & engineer? Are there any specific violations or compliance issues with this design?