mtdt
- Lynchburg, Va, USA
Here’s my question:
We have multiple state owned & operated self serve fuel dispensing sites. According to 2014 NEC 514.11 all power, communication, etc needs to be shut down when the emergency stop is activated. We accomplish this with a contactor that disrupts power (& neutral) to the power panel that supplies all the circuits to the fuel island. The E stop switch keeps the contactor energized and, when activated, de-energizes the contactor.
We also have a fuel equipment/tank monitoring system that monitors tank levels, leak detection, etc. This TMS uses intrinsically safe field wiring and sensors. The design folks have powered the TMS from the fuel system power panel. When the Estop is activated the TMS is also shut down which causes us to loose all ability to know what's going on at the fuel equipment. My view is that since the TMS field wiring is intrinsically safe, it should be exempt from the shutdown requirements in 514.11. Neither this article or article 504 (intrinsically safe systems) address this. What is your interpretation? I believe the2017 NEC may clarify this.
Thank you for your generous contribution the the electrical trade with all the resources you provide.