sluton

Member
What does the NEC Code say, along with the Pro's and Con's of running an E-Stop through the input of a PLC system?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: E-Stops in industrial control circuits

That is not covered by the NEC. In my opinion, a true e-stop should not use the PLC to shutdown the equipment. We use a hard wired relay for e-stops on PLC controled systems. The relay drops out the power to all of the output modules and to the motor starter coils. The relay is wired using only normally open contacts and the coil is normally energized. Any coil failure, e-stop circuit failure, or operation of the e-stop switches will cause a shut down.
Don
 

friebel

Senior Member
Location
Pennsville, N.J.
Re: E-Stops in industrial control circuits

To: sluton, and don_resqcapt19,
I totally agree with you Don, never use a PLC program for an emergency shutdown system.
I worked for a large Chemical company for many years, and we had a program, called a Process Hazards Review. It was our company policy, world-wide not to depend upon a software program for an emergency shutdown. It was always hardwired, as you said Don, with a hardwired relay etc.
 

gregoryelectricinc

Senior Member
Re: E-Stops in industrial control circuits

I agree, ALWAYS hardwire an E-stop. However, most PLC's will allow you to use the E-stop as an input also. This is sometimes useful for warning buzzers, flashing lights, etc. Usually these inputs are isolated from all the rest of the PLC's inputs so they stay active when the E-stop is pushed.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: E-Stops in industrial control circuits

I just read an article in the AB journal on estops and NFPA 79. the article stated that NFPA 79 now allows estops to be done with a PLC instead of a hard wired relay.
Here is a link to the article
http://www.ab.com/abjournal/sept2003/departments/technology_watch/index3.html

I still like hardwired, but PLCs are very reliable, but I have seen several develop fatal errors. I suppose you could have the estop drop out on an error
 

karagory1

Member
Re: E-Stops in industrial control circuits

For emphasis I think that it should be noted that one "typical" PLC would not be acceptable.

"This means users can replace hardwired circuits with redundant standard PLCs, safety PLCs and safety networks."
 

vtrel

Member
Location
Michigan
Re: E-Stops in industrial control circuits

I recall going to an AB safety seminar and being told E-Stop must be hard wired. It came from a robotics safety standard. Safety relays and switches just redundently check the circuit and device.
 

hillbilly

Senior Member
Re: E-Stops in industrial control circuits

IMO Hard wired is the only way to go. A life may depend on that machine stopping. The E-Stop has to be accessible, simple, and foolproof. In the past I used detent type pushbuttons to drop out the holding contacts on the motor starters and run relays. The machine couldn't be re-started unless the detent button at the incident location was manually reset. This prevented a remote operator from re-starting a motor or process. Some of the process lines were up to 300' long with numerous motors and drive systems. I personally would never depend on a PC to provide E-Stop.
steve
 

pwhite

Senior Member
Re: E-Stops in industrial control circuits

i think there is a mis-understanding of what the article said.

you can replace the hardwired relay controls with a safety plc controller. this is different from a standard plc. the safety plc is specifically designed for e-stop circuits and can allow the user to run a coax type cable from the main processor to remote modules. this eliminates all the wires from the e-stops back to the central location. depending on the type safety plc module used, you can also assign safety matts, light curtains, and other safety items as the inputs, and a second module for the outputs to control the machine operation (such as conveyor motors)based on what safety device was tripped.

the safety plc can also communicate back the the machine control plc via its communication cable.

pilz makes several versions of e-stop controllers and safety plc's. we quoted a system which required 30 of their safety plc's.

i hope this information helps.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: E-Stops in industrial control circuits

thanks Pwhite for clarifying that on the safety PLC. If this is a an area a reader is interested in, then the AB article should be read.
 