Thats true,
I really don't know the answers to those questions.
At this point I just need to know if the code around 1990 required seperating the grounds and neutrals in a residential generator panel...
Is the generator frame bonded to the neutral at the gen set?Thats true,
I really don't know the answers to those questions.
At this point I just need to know if the code around 1990 required seperating the grounds and neutrals in a residential generator panel...
It was not installed to code. In 1990 all sub panels had to have the grounds and neutrals separated. Generator panels were not a separate section or mention in the NEC really at the time. These were just classified as sub panels.
But this is just from personal remembering. I don't have a copy of my old code books from way back when.
Sent from my iPhone using Tapatalk
I have a 1990 NEC in my lap. 250-6 addresses portable and vehicle mounted generators. Article 445 is Generators and they must comply with 250 and 230 (among others). 250-23(a) states a grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means.
Thank you very much!
I didn't want to buy a 1990 code book just to look up this question!
Very much appreciate it!![]()
So I was still right about them needing to be separated