Re: Earth fault
Without knowing much about UPS stuff, common sense makes me think branch circuit ground faults trip GFCI's & breakers, and would leave that UPS running on batteries all the time.
But, a slow leak through load side equipment may not trip anything. Maybe a controlled shut down of load-side equipment, at some point would make it go away?
The UPS manual may suggest other causes for that indicator, or suggest reseting or swapping the UPS, after a controlled shutdown of attached loads.
If the branch circuit is faulting to earth/ground, without tripping breakers, then equipment cases will also stay energized.
If equipment grounding prongs and cases are energized with the branch-circuit phase then placing a volt meter neutral to ground may show line voltage. (previous H-G idea deleted)
But, doing that with a Wiggy's (solenoid tester) could trip GFCI's and crash the connected data processing loads. Common inductive multimeters don't usually draw enough current to trip GFCI's.
[ December 25, 2005, 08:30 AM: Message edited by: ramsy ]