Re: Earth Ground for ESD
Originally posted by tomc5: I thought for sure any static charge grounding would want a LOW impedance to prevent a high buildup?
I think you may note that Don said 1,000,000 ohms
or less.. If there is a path for current to flow, and if the resistance of that path is not extraordinarily high (i.e., more than a million ohms), then the static charge will find its way to planet Earth, and be discharged. However, please note that so long as there is flow in the pipe, there will be a source for static charge (see discussion below).
. . . static charge buildup problem . . . with a section of glass tube . . . the piped fluid is a non-conductive . . . oil . . . .
One of the original experiments that led to the discovery of many electrical principles involved rubbing a (non-conductive) glass rod with a (non-conductive) silk cloth. The cloth imparted a static charge to the rod. You may be looking at a similar situation. What I am saying is that you should not be confused by the phenomenon occurring with a non-conductive fluid in the pipes.
The problem you are facing relates to the non-conductive nature of glass. The ?rubbing? of oil against the glass may be imparting a charge to the glass. But once there, the charge might just stay there. Charge will not easily be conducted off the glass, and onto some other surface. The glass might be in intimate contact with the metal pipe, and the metal pipe might already be in intimate contact with planet Earth. But the charge is not being conducted from glass to pipe to dirt, because the glass is not a good conductor. So adding any type of grounding conductor (e.g., from the pipe to a ground rod) will not change the situation. Nor will bypassing the glass section with an internal or external connection between the metal sections on either side of the glass section.
You are certainly outside the realm of the electrical power industry. The NEC will not help you with this problem. There may be a member of this Forum who knows how to handle the problem, but I am not that member. Have you tried speaking with other members of your own profession? Surely someone else has seen this situation before, and has already figured out a solution. Good luck.