Muzammil.qazi
Member
- Location
- Karachi
- Occupation
- Electrical Design Engineer
In our project we have meshed/interconnected several earth pits together (inter-pit bonding / meshing). The execution team used 16 mm² copper cable upon my suggestion, as I heared from some where for the bonding conductor. Now the client while executing asking basis of this selection, he insists that such interconnection should use much larger conductor (for example 95 mm² copper). I am new with 1 year experience only, and completely disturbed how to tackle him. Pls help.
My questions:
My questions:
- Does any internationally recognized standard (e.g. BS 7430, IEC 62305‑3, or any other) explicitly mandate a fixed conductor cross-section (e.g. 25, 50, 95 mm²) when meshing or bonding earth-pits ?
- If there is no such fixed-size clause, what is the correct standard-based method to select the conductor size for earth-pit interconnection ?
- How does adiabatic equation helps in this ?