Earth Resistance Testing
Where would the EGC return to in an ungrounded system?
Nowhere, the EGC in an ungrounded system just bonds all the non-current carrying metal parts.
If the transformer is a source then how could it be connected to ground without a bonding jumper?
None of the transformer secondaries would be connected to earth, but the case of the transformer would be connected to the EGC and the EGC connected to earth.
What is the purpose of bonding all of these if no current will flow?
If in my case I sketch if the EGC was connected to the secondary as shown would current theorotically then flow back to the source in the case of a ground fault even know the source was not bonded to ground?
Yes, but it would not be an ungrounded system. The connection to a grounding electrode is incidental. The purpose of the EGC is to provide a path for ground fault current to flow that is not dependent on current flowing through earth and the grounding electrode. Ground current will flow through the EGC whether or not it is connected to ground. Ground current does not have to flow through the earth.
So what about in HRG system? We have a HRG system that I know has EGC's going to each motor. The ground fault current is supposed to be limited to 5A. If the EGC's were connected directly to the transformer nuetral then we would have more than 5A and therefore trip breakers. I'm therefore assuming that resistor must be between the EGC's and the tranformer nuetral to limit this current to the correct current.
What is the purpose behind the NEC requiring an earth resistance of no more than 25ohms in section 250.56?
And may I add it does not even require 25 ohms, once you drive add another electrode you are done regardless of it being 4 ohms or a 100 ohms.
Ok then to clear up all my confusion and gain the correct understanding, what is the main purpose of the ground grid that is installed around each one of the electrical rooms containing a 4160-480 substation in my plant?
These ground grids are then tied into the rest of the plant grounding.
If there is a ground fault on the incoming 4160V, then if the 4160V source is remote, a portion of the fault current will return through the earth. Current flowing through the earth will raise the voltage of the grid with respect to the remote source ground point. The ground grid makes the substation surface voltage fairly uniform and close to the voltage of the grid, reducing the voltage that would exist between a person's feet (step-voltage) and between his feet and hand while touching a grounded structure or equipment (touch-voltage).
In other words, the grid is more for equi-potential bonding, like with swimming-pool bonding, than actual earthing.
Remember, it's not just voltage that is dangerous, it's differences in voltage between touchable points or surfaces.
OK so I think I have confused myself even further by researching this matter more in depth.
I was always under the impressin that a grounding electrode or ground grids main purpose was to provide a low resistance path to earth. It was this low resistance path to earth that allowed fault current to flow or return to its source. It sounds like after reading some of these responses that the main purpose of these grounding electrodes is to provide an equal voltage potential at all areas that are connected to ground in order to limit the step and touch potential. Does this sound like a reasonable summary. Is there anywhere I can find more information on this subject.
The second half of this subject which I am struggling with is understanding exactly what physically determines a grounded system vs an ungrounded system. Part of this confusion is distinguishing the different roles betwenn an equipment ground conductor (EGC) and an grounding electrode conductor (GEC). What is the key between distinguishing these two?
A grounded system I understand to have either a bonding connector between an electrode conductor and source or to have an EGC between source and equipment. If there is no bonding jumper between ground and source but yet there is an EGC between source and equipment then this is still a grounded system.
What if there is a bonding jumper between ground an source and no EGC and there is a L-G falult between a cable and a steel beem which is grounded to earth. Will the fault current travel through the beam through earth and back to the source with enough current to trip an OCPD?
The current has to get back to its source, not the earth. The will carry some of the current back to the source if it is a grounded system, but it will rarely carry enough to open the OCPD. It also does not do a good job of providing an equal potential. In areas where you need equal potential, like substations and the like, there is a bonding grid that provides the equal potential.
The physical determination of a grounded system is the fact that one of the circuit conductors of a grounded system is connected to the grounding electrode(s) via a grounding electrode conductor. The equipment grounding conductors connect the metal parts of the equipment to the system grounded conductor via the main bonding jumper and to the earth via the grounding electrode conductor. The fault clearing work is done by the equipment grounding conductor and not by the grounding electrode conductor.
If there is no system conductor connected to a grounding electrode then the system is not a grounded system.
If we are talking about system of 600 volts or less, then it is not likely that the earth will carry enough current to open the OCPD. If you are talking about medium or high voltage systems, then it is likely that the earth will flow enough current to open the OCPD. It is ohms law at work...the higher the voltage the more current that will flow though a given resistance.
OK as I am researching this more I am begining to understand this subject a little better. Grouding is a difficult subject to grasp:D
Let me give another example:
Lets say I have a metal enclosed cabinet in the field with electrical equipment insisde and a 480V power supply to this cabinet. Lets say that this cabinet is grounded by taking a ground conductor from the frame of the cabinet to a ground rod in the earth.
Now if there is a L-G fault on this cabinet I now understand that because the earth is such a high resistance, the grounded connection to earth will not clear this fault. Lets suppose for some reason there is not an EGC to this cabinet an therefore the fault does not clear.
So without this fault clearing even though the cabinet is grounded through earth there will still be a dangerous voltage on the cabinet surface which will be 277V or close to it depeding on the resistance of the fault point and little current flowing through earth.
So if someone were now to walk up and touch this cabinet lets say from standing 3ft away would they be exposed to this 277V and be shocked. If the answer is yes then what is the point of even having a grounded earth connection at this cabinet.
I understand that this cabinet should have an EGC and this would hopefully clear the fault and eliminate this voltage on the cabinet. But why ground this cabinet to earth if this ground connection will not do anything to eliminate the dangerous voltage potential? Am I understanding this right?
There is no electrical or safety reason to provide a grounding electrode at that cabinet. The only thing that will remove the hazard is to clear the fault by tripping the OCPD...the only thing that will do this is an effective EGC.
Mull,
Two great books I think will answer all your questions;
1. Soars, Book on Grounding and Bonding.
2. Getting Down to Earth.
You can order the Soars book on the NFPA web site, great book, will answer all your questions and more. Getting down to Earth is free at Meggers web site, you just have to register.
Hope this helps.