tom baker said:But for a motor, the size of the EGC is based on the size of motor overload protective device see 250.122(D). Motors will typically have the short circuit device (CB or fuse) higher than that required in 240.4 (IE protect a conductor at its ampacity) to allow the motor to start.
That is an instantaneous trip device. It is not an overcurrent protective device because it does not provide protection from overloads. It only provides protection from short circuit and ground faults and can only be used as part of a listed combination motor starter.infinity said:250.122(D) mentions a motor short circuit protector, what is a motor short circuit protector? Doesn't sound like a fuse or inverse time CB.
don_resqcapt19 said:That is an instantaneous trip device. It is not an overcurrent protective device because it does not provide protection from overloads. It only provides protection from short circuit and ground faults and can only be used as part of a listed combination motor starter.
The instantaneous trip breaker and the motor circuit protector are the same thing...a magnetic only device. No thermal device for overloads.infinity said:So it isn't an instantaneous trip circuit breaker but another device that operates in the same fashion.
don_resqcapt19 said:The instantaneous trip breaker and the motor circuit protector are the same thing...a magnetic only device. No thermal device for overloads.
Don