Earthing bar class 1 division one or two

reyamkram

Senior Member
Location
Hanover park, il
In a class one division one or two hazardous location the earthing bar material should be copper or can you use a different type of material the bar that is connected to the grounding electroconductor and then the building Steel thank you for all and any information
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
In a class one division one or two hazardous location the earthing bar material should be copper or can you use a different type of material the bar that is connected to the grounding electroconductor and then the building Steel thank you for all and any information
I don't believe there are any special rules about this for classified areas. But what would the point be?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Any grounding/bonding requirements, unique to Class I locations, are found in Section 501.30. Otherwise grounding simply complies with Article 250.

The term “grounding electroconductor” is unrecognized in Article 250 raising the question of purpose.
 