I am familiar with table 430.52 and its requirements and the differences between the types of short circuit protection. This question is a matter of true life real world application:
Motor FLA = 48A
This is an AC Polyphase motor other than wound rotor motor therefore:
Max MCCB (inverse time breaker) setting/size = 2.5*48 = 120A.
I now go to the breaker store and ask the guy for a catalog he gives me the attached chart. With out thinking I look to choose 125A size because it is the next size up from my calculation. But then I notice, this particular MCCB has options for adjustable thermal (inverse time) and adjustable magnetic (instantaneous) trips. The range for the Mag trip is 625A - 1250A. If I look at my FLA and multiply by 800% which is under the Instantaneous (MCP breaker) column of 430.52 I get a maximum rating of 384A. That gets me wondering. Should I just buy the Max continuous amps of 70 breaker since the mag trip adjustment is in the range for of the maximum allowed instantaneous setting?
I would never have second guessed the 125A frame selection if I didn't see the Mag trip range.
Motor FLA = 48A
This is an AC Polyphase motor other than wound rotor motor therefore:
Max MCCB (inverse time breaker) setting/size = 2.5*48 = 120A.
I now go to the breaker store and ask the guy for a catalog he gives me the attached chart. With out thinking I look to choose 125A size because it is the next size up from my calculation. But then I notice, this particular MCCB has options for adjustable thermal (inverse time) and adjustable magnetic (instantaneous) trips. The range for the Mag trip is 625A - 1250A. If I look at my FLA and multiply by 800% which is under the Instantaneous (MCP breaker) column of 430.52 I get a maximum rating of 384A. That gets me wondering. Should I just buy the Max continuous amps of 70 breaker since the mag trip adjustment is in the range for of the maximum allowed instantaneous setting?
I would never have second guessed the 125A frame selection if I didn't see the Mag trip range.