Easy: loading 750kW cat in a 0.95pf bldg

Status
Not open for further replies.

julesm

Member
can this 750kW standby generator provide 750kW/0.8 = 937kVA
OR 750kW/0.95= 789kVA?

Caterpillar provides the 0.8 number. Building pf is 0.95.

Thanks!!
 
The generator has the capacity to provide the 937 KVA. If the building only uses 789 KVA, then the generator will have spare capacity of 148 KVA. That said, the generator is still limited to 750 KW. So if the building's .95 power factor is based on a real load in excess of 750 KW, then the generator will not be able to handle the entire building. In other words, the "spare capacity of 148 KVA" I mention above has to be primarily "reactive power" loads, and not "real power" loads.
 
My rough understanding of this topic:

You have two limiting factors in play: the alternator which can only provide so many KVA, and the prime mover which can only provide so many KW down the shaft to the alternator.

You cannot exceed either the KVA rating or the KW rating without putting some part of the system into overload. If the power factor of the load is really bad, then you overload the alternator with excess current, while the prime mover is loafing along well below its maximum power rating. If the power factor of the load is really good, then you overload the prime mover without reaching the current limit of the alternator.

-Jon
 
Thanks Charlie B and Winnie! Very clear, helpful responses. Especially the alterntor/pm breakdown. Makes it clear to me how rusty I am about how these things really work.
Take Care,
JM PE
 