The generator has the capacity to provide the 937 KVA. If the building only uses 789 KVA, then the generator will have spare capacity of 148 KVA. That said, the generator is still limited to 750 KW. So if the building's .95 power factor is based on a real load in excess of 750 KW, then the generator will not be able to handle the entire building. In other words, the "spare capacity of 148 KVA" I mention above has to be primarily "reactive power" loads, and not "real power" loads.