Easy one: Do you need an additional electrode at a solar canopy/carport?

Status
Not open for further replies.

ryangittens

Member
Location
usa
Say you have a metal solar canopy/carport in your parking lot that's 100ft away from your building's service which you are going to tie into. Could you just use the EGC coming off the array for grounding or do we need an additional GEC/Electrode near the structure itself (or have the electrode be the structure itself)?

We're in the 2011 NEC cycle until January.

The 2017 code says, "A building or structure supporting a PV array shall have a grounding electrode system installed per NEC part III of 250." I feel like the existing electrode system would be adequate as it goes on to say that additional electrodes at ground and roof-mounted arrays are optional.

Would you agree?


Thanks!
 

Smart $

Esteemed Member
Location
Ohio
Generally speaking, any electrified separate structure requires a grounding electrode system per 250.50.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Under the 2011 code, no I don't think an electrode is required if the circuit is a single branch circuit. (If you have an AC aggregation panel for multiple inverter outputs then 250.50 requires an electrode.) Under all other recent code cycles it would be required by 690.47(D) or (B).
 