FionaZuppa
- AZ
- Part Time Electrician (semi retired, old) - EE retired.
I am coming across Eaton AF OCPD's that simple fail upon test (button). Usually a hummmm w/o tripping. Anyone else seeing this issue?
Trip how? Test button is a monthly test.Just my opinion , but I don't think they want them to trip to often. Otherwise jurisdictions will strike them from their local codes. They have a vested interest in selling more of them.
Perhaps the manufacturer fine tuned it a little to much.
When you push the button it test the "trip" mechanics of the breaker.Trip how? Test button is a monthly test.
Actually it probably is testing a certain amount of the electronics and most likely energizes a trip coil. Since OP says it hums but doesn't trip there likely is a mechanical problem though.When you push the button it test the "trip" mechanics of the breaker.
BTW How many get tested monthly?
??even if that did happen, what does it really 'test' Finoa?
~RJ~
i suspect even the manufacturers can't quantify with any solid electrical theory FionaThe test button creates a small short which is then supposed to trip the OCPD. It's testing that the darn thing works as advertised. I suspect it's not creating an actual arc test, but the test button should trip the OCPD. Is it a tronics issue, or a mechanical issue, I can't say for sure.
yes it's not unusual Jon , and the consumer protective agencies have the right to call them out on it.Even big (supposedly) reputable companies cheat on requirements in order to meet sales quotas. The more complex and demanding the requirements become (like the insistence on installing devices that can accurately and reliably detect an arc fault without nuisance tripping from, say, a vacuum cleaner), the more likely it is that manufacturers are going to cheat.
Dual function very possible. some the CAFCI's that don't require the load neutral be connectedI doubt it Kwired
If i had to guess, it's probably throwing a certain ~R~ value across the toroidal coil, same as a gfci
otherwise, those DF's would have to have two test buttons......
~RJ~
then when is it 30ma, and when 5ma kwired?Dual function very possible. some the CAFCI's that don't require the load neutral be connectedmaybeprobably not?
You can't get Eaton?Receently had 2 Eaton afci's I installed years ago fail but unsure if it had to do with water damage or not, the panel had some moisture from duct seal failing. Both went at the same time and there were electrical storms in the area. Replaced with HOM square D's. One wouldn't trip with the test button, other wouldn't reset.
I didn't think you were supposed to mix manufacturers breakers with different manufacturers panels.Receently had 2 Eaton afci's I installed years ago fail but unsure if it had to do with water damage or not, the panel had some moisture from duct seal failing. Both went at the same time and there were electrical storms in the area. Replaced with HOM square D's. One wouldn't trip with the test button, other wouldn't reset.
Correct. At least according to the manufacturers.I didn't think you were supposed to mix manufacturers breakers with different manufacturers panels.