Hi! I'm grateful for the opportunity to post here and read your opinions.
I have a 1994 built house and the panel is missing the label. I identified the panel as a T&B TBB20. I got a copy of the label.
Some clown finished the basement himself and put square D HOM120 breakers on his #14 wiring. Wife must move into the house immediately, so this is an emergency. I asked an electrician and he told me to get BR115, and even if the HOM breakers were properly sized he would not want this situation in his house or anything he worked on. Now I know I am "supposed" to put CL in this panel. But I think the situation is better. The BR are easy to get in stores immediately, the CL not so much.
Most of the T&B breakers in this panel are not marked as to their type on their face and I had to pull them out to get this information from a sticker on the side with the T&B logo and model number (TB115, TB120, etc.) There are a few TB120 which are marked properly on the face but their switch handle varies slightly with its legend and mold. These breakers have a different UL file number than the others. It could be that T&B actually had different manufacturing lines or retooled the parts, or they could have been reselling breakers that other companies made.
After comparing both sets T&B breakers with the BR breakers I got, they look the same to me from the outside. There are only minor variances in the features of the plastic, rivets are in exactly the same place, same warnings molded into the housings in the same place but maybe the typeface differs, etc.
Most interesting to me is that the new BR breakers have the same UL file number E7819 as the first set of T&B breakers and this file number is assigned to Eaton now. I'm pretty sure the BR is a product line Eaton acquired and maybe another company acquired it before Eaton. The file number on the other set of T&B breakers is not found. The file number on the panel and main breaker belongs to Eaton now. I haven't looked into the CSA listings because I'm not in Canada, but they are all different.
I know that I need the CL breakers to pass an inspection. This work shouldn't pass anyway for other reasons. I am more worried about safety, and whether the BR breakers in this panel are a hazard.
Are there any real differences inside the BR and CL breakers, or the BR and old T&B breakers? It seems reasonable to me that if Eaton tested their BR breaker in all those different panels, that the usual customer of BR shouldn't have to pay for all that lab work and paperwork, so they could give them a different marking and have the CL customers pay for all this.
I have a 1994 built house and the panel is missing the label. I identified the panel as a T&B TBB20. I got a copy of the label.
Some clown finished the basement himself and put square D HOM120 breakers on his #14 wiring. Wife must move into the house immediately, so this is an emergency. I asked an electrician and he told me to get BR115, and even if the HOM breakers were properly sized he would not want this situation in his house or anything he worked on. Now I know I am "supposed" to put CL in this panel. But I think the situation is better. The BR are easy to get in stores immediately, the CL not so much.
Most of the T&B breakers in this panel are not marked as to their type on their face and I had to pull them out to get this information from a sticker on the side with the T&B logo and model number (TB115, TB120, etc.) There are a few TB120 which are marked properly on the face but their switch handle varies slightly with its legend and mold. These breakers have a different UL file number than the others. It could be that T&B actually had different manufacturing lines or retooled the parts, or they could have been reselling breakers that other companies made.
After comparing both sets T&B breakers with the BR breakers I got, they look the same to me from the outside. There are only minor variances in the features of the plastic, rivets are in exactly the same place, same warnings molded into the housings in the same place but maybe the typeface differs, etc.
Most interesting to me is that the new BR breakers have the same UL file number E7819 as the first set of T&B breakers and this file number is assigned to Eaton now. I'm pretty sure the BR is a product line Eaton acquired and maybe another company acquired it before Eaton. The file number on the other set of T&B breakers is not found. The file number on the panel and main breaker belongs to Eaton now. I haven't looked into the CSA listings because I'm not in Canada, but they are all different.
I know that I need the CL breakers to pass an inspection. This work shouldn't pass anyway for other reasons. I am more worried about safety, and whether the BR breakers in this panel are a hazard.
Are there any real differences inside the BR and CL breakers, or the BR and old T&B breakers? It seems reasonable to me that if Eaton tested their BR breaker in all those different panels, that the usual customer of BR shouldn't have to pay for all that lab work and paperwork, so they could give them a different marking and have the CL customers pay for all this.