Has anyone heard that Eaton is dropping the convention of using notched bus stabs to accommodate tandem breakers? The installer of this panel insists that non-CTL tandem breakers can be installed in this panel at any stab location, though none of the stabs is notched.

If this is the case, doesn't anyone have any documentation from Eaton?

If this is the case, are other manufacturers likely to follow suit?
 

Attachments

  • RIMG0123 (Large).JPG
    RIMG0123 (Large).JPG
    281.2 KB · Views: 22
  • RIMG0146 (Large).JPG
    RIMG0146 (Large).JPG
    283.5 KB · Views: 23

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
The installer of this panel insists that non-CTL tandem breakers can be installed in this panel at any stab location, though none of the stabs is notched.
Correct, Non CTL breakers do not have the rejection clip and can be installed in any location on the bus. CTL on the other hand have the rejection clip and can only be used on notched bus locations.
Non-CTL breakers (ie BR1515 $27) are a lot more expensive than the CTL type (ie BD1515 $16) though.
Also caution should be had to avoid overloading panel with a lot of non-CTL breakers,
Non that I've seen. Most have added more than the 42 circuits. My favorite cheap siemens 200amp is a 3048
Eaton listing seems to max at 42. Others seen as high as 80. I do like the Siemens as I can get tandem AFCI for them.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I do like the Siemens as I can get tandem AFCI for them.
Siemens Line card shows UL Type QTA
Tandem AFCI breakers without the rejection feature can be installed in any panel that lists that breaker type or where a substitution letter exists for that breaker type
Has anybody seen what a substitution letter looks like?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You might want to take a look at this thread. I find the entire issue to be somewhat confusing due to the markings on non-CTL breakers.

 