In my opinion, the circuit breaker Eaton LSIG- for instance- is provided with two short-delay possibility: one for short-circuit between phases [tsd] and one for phase to ground [tg].The letters on the selector indicate the delay combination of these.
Let's say for tsd=inst. [instantaneous] between phases and tg=300 ms delay for ground fault the L position has to be selected. See:
file:///C:/Users/user/Downloads/TD012019EN.pdf
In my opinion, the circuit breaker Eaton LSIG- for instance- is provided with two short-delay possibility: one for short-circuit between phases [tsd] and one for phase to ground [tg].The letters on the selector indicate the delay combination of these.
Let's say for tsd=inst. [instantaneous] between phases and tg=300 ms delay for ground fault the L position has to be selected. See:
file:///C:/Users/user/Downloads/TD012019EN.pdf