I was more worried about the caps.
It's a valid concern in my opinion.
If the PFC is for fixed speed motors on a per motor basis, load side of the starter you said, automatic correction should not be required. You are correcting for the motor reactive component of the current drawn. And that doesn't change much.
But, if you have variable speed drives or other non-linear loads, the supply voltage will be distorted to some extent. It may even be distorted on the supply side without anything on your plant running. That distortion is harmonics. Multiples of the supply frequency. Higher frequencies mean higher currents in capacitors.
To what extent it increases the current in the capacitors depends on the degree of distortion but I've come across a number of cases it has resulted in failures. Some spectacularly so. In one paper mill there was bulk PFC with automatic control. Every single bank had failed - I mean blown the guts out of it sort of failed. I've seen similar sorts of things in a few places. And sometimes trivial but inconvenient like the capacitors in every single fluorescent light fitting failed.
I can't say it will be like that for you. My background is power electronics so I suppose it's somewhat inevitable that I come across situations where the level of harmonics may be higher that average. That said, they are often not very good at utility level. And you can't do a lot about that.
We are not all that often involved in projects where PFC is required but when we are I always fit de-tuning reactors. These are calculated to block frequencies above 5th harmonic, 250Hz in our case.
But that may not be a practical proposition for you, not least for cost considerations.
So what to do? A power quality analysis would help to define the extent of the potential problem. Or absence of it.