- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
I just read an article in EC&M about a factory that had been operating for 40 years with voltages at 194v phase to phase and 112v phase to ground. Apparently there is a 480/208-120v labeled transformer that was tapped incorrectly. What I don't get is the writer stated the trany was tapped for 480v so he changed it to 460v tap and the voltages on the secondary went 208/120.
If the trany is marked 480 why would you have to wire it to 460v to get the proper voltage
Here is the article but I think I got the gist of it
If the trany is marked 480 why would you have to wire it to 460v to get the proper voltage
Here is the article but I think I got the gist of it