EC&M Forensic Case Book Article

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I sent an e-mail to the author....he replied that testing showed that the box did not have a good connection to ground, but did not provide any details.
Of course it did not have good connection. These guys always have the answer you cannot cross examine unless you were present.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
At one point the author discusses how the baby monitor was ruled out as the source of the fire, because when it was opened there were no signs of a fire on the inside.
Yet the receptacle is being blamed, when it also does not have any signs of a fire internal to its box/enclosure.
Jim, there is quite a "disconnect" that happens in the authors' language about the receptacle and box/enclosure.

The author(s) claim there is a clear violation of the NEC in what they show, but to my eye, I am not shown that violation in Photo 2. The author(s) claim that the NEC requires a "wire" for a ground connection is, simply, the author making up his own Code.

Now, following on Don's paraphrase of the author's email response about "testing". . . if continuity, and / or polarity, testing resulting in an electrical lack of continuity in the Equipment Grounding Conductor back to the Main Bonding Jumper in the Electrical Service Disconnect did, in fact, exist, that should be stated, AND, the forensic examination continued to reveal the point, or points, of dis-continuity. It may be as simple as showing the lack of an auto-ground feature in the receptacle device.

We can't know, because the "proof" offered is not proof at all, and the rest of the article does not include any information to support the conclusion of the authors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
He was very quick to respond to my email question, as have been most of the authors of EC&M articles....others could send him additional questions:)
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
.. ..others could send him additional questions:)
I left the article author(s) the 1999 NEC 250-118(9) rule quote, including the rule about the EGC "enclosing" the circuit conductors, in a comment that is now up at the www.ecmweb.com article page comment section, along with a question about the receptacle device yoke features.

I would imagine he is on a crash course of learning about the 1999 or 1996 NEC Article 333 Armored Cable wiring method, but, I can't be sure what this expert actually knows based upon the muddled language of the published article.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The following is part of one of the authors comments.
No ground means neutral must take up the slack. It's often not strong enough to do this without getting very, very, very hot.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Now they are censoring comments on EC&M.

I commented as to this

"No ground means neutral must take up the slack. It's often not strong enough to do this without getting very, very, very hot."




I asked where he gets his info from.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
There is a time lag before the comment is posted because EC&M has to "review" your comment by a human, first. Do you think that is why it is not live yet?


Nope its been several days.

I think they have mud on their face at this point!

Please with a comment like this


"No ground means neutral must take up the slack. It's often not strong enough to do this without getting very, very, very hot."

What electrician , engineer or other knowledgeable person would make such a comment.
Then to cause a EC harm!


Fishey
 