stickboy1375
Senior Member
- Location
- Litchfield, CT
I read this and find this untrue... anyone else?
? NEC 225.39(B) requires for a two-circuit installation that the disconnecting means be rated not less than 30 amperes. Now comes our first problem. You are using 12 AWG conductors in your feeder, and the two-circuit installation requires a 30-ampere disconnect. (Strike one!)
http://www.ecmag.com/index.cfm?fa=article&articleID=8918
? NEC 225.39(B) requires for a two-circuit installation that the disconnecting means be rated not less than 30 amperes. Now comes our first problem. You are using 12 AWG conductors in your feeder, and the two-circuit installation requires a 30-ampere disconnect. (Strike one!)
http://www.ecmag.com/index.cfm?fa=article&articleID=8918