Concrete-encased electrode
Q: Does the National Electrical Code (NEC) permit a grounding-electrode conductor smaller than 4 AWG copper for a concrete-encased electrode for a 60-ampere, 3-wire, 120/240-volt service? The service conductors are three 6 AWG copper with THWN insulation.
A: There is nothing in Article 250 that allows the grounding-electrode conductor to be smaller than 4 AWG copper. There also is nothing in Article 250 that requires the grounding-electrode conductor from the reinforcing steel to be larger than 4 AWG copper.
Article 250.66(B), which states the grounding electrode for a concrete-
encased electrode does not have to be larger than 4 AWG copper, covers the connection to the concrete-encased electrode.
Where the concrete slab in contact with the earth does not contain 20 feet or more of ?-inch or larger reinforcing rods, the concrete-encased electrode may consist of at least 20 feet of bare 4 AWG copper placed near the bottom of the concrete foundation. Article 250.52(A)(3) permits this substitution of wire for reinforcing rods. Notice the minimum size wire electrode is required to be 4 AWG bare copper
I just got around to reading this issue of Oct.07 Electrical Contractor Magazine and wondered if everyone agrees with his answer?