is it necessary for four 7.5 HP fans?
probably not in the strictest sense of the word, but the real answer is it depends. how many other non-linear loads does the facility have? how many induction motors does it have? What % of total load is non-linear? what size is the utility transformer?
IEEE 519 dictates the requirements for allowable harmonics any user of a utility can "inject" back onto the grid, relative to the demand load and service transformer. the point of measurement is defined as the point of common coupling (POCC) and typically exists on the bus where the utility connects to the owner's equipment. reading the standard would lead one to think they shouldn't care until the utility sent them a letter stating they are out of compliance. but the best approach is the be proactive and the supplier of the AHU has an interest in not being the straw that broke the camels back, as they do not have intimate knowledge of the system. they hedge by making sure their equipment contributes as little harmonic content as practical.
There are many ways to comply with IEEE 519. you could install a very large filter at the top of the power distribution system or you can distribute small filters at motor controllers and other large non-linear loads. alternatively several medium-sized ones at strategic locations in the power system. the important thing to note here is if you have many non-linear loads without any mitigation whatsoever, their effects are additive and, if significant, could become a ghost in the machine so to speak. the best way to know if you have a problem is to have someone study the system, ask questions, and measure the harmonics, suggesting remediation if needed.
all of this being said, they serve as cheap insurance/surge protection for the VFD(s) and any other electronics beyond the CPT. albeit, they are likely not as effective as a dedicated surge protective device.