Not sure if the title makes sense here but I am designing a project in Illinois that needs an EE stamp. They have redlined a few of our plans stating the wire size needs to be sized up because we have to use the 60C column in 310.15 for conductor ampacity. Here are a few of the different situations where we have this issue:
![1689954054928.png 1689954054928.png](https://forums.mikeholt.com/data/attachments/30/30159-ae86343a55994092ce21171effc4f9d6.jpg)
And when I asked him about it, all he said was this "See NEC 110.14(C)(1). You can only use the 90 degree C for derating calculations. Since your calculation came out higher than the 60 degree C column, you have to use the 60 degree column for the ampacity."
Could someone help explain this to me because I don't understand how this works. I might be missing some info so if you need extra clarification let me know.
![1689954054928.png 1689954054928.png](https://forums.mikeholt.com/data/attachments/30/30159-ae86343a55994092ce21171effc4f9d6.jpg)
![1689954175228.png 1689954175228.png](https://forums.mikeholt.com/data/attachments/30/30160-3dab9390ed74e80814921abb16d347a9.jpg)
Could someone help explain this to me because I don't understand how this works. I might be missing some info so if you need extra clarification let me know.