Strahan said:AC or DC? I have seen countless times where a fault occurs on a DC power supply drawing the voltage level down. Once the fault is determined and fixed the supply returns to nominal level. Of course this is on lower voltage scale typically 24vdc.
gar said:080915-2114 EST
An ideal voltage source has an absolutely constant voltage output. This is what you work with theoretically in an equivalent circuit.
A real world voltage source will generally be assumed to be an ideal voltage source with some series internal impedance, or an ideal current source with a shunt internal impedance. You can use either as your source.
The short circuit current is determined by the ideal voltage source, and its internal impedance in series with whatever is the external short circuit impedance.
Yes.......mull982 said:When a fault occurs in a system does the voltage supplied by a voltage source decrease heading towards 0V?
Is this decrease in voltage a result of the high current across the voltage source impedance causing this voltage to drop?