161102-1123 EDT
The purpose of this comment is to show why electrical isolation should be used in an RS232, 422, or 485 communication path. If not isolation, then a sacrificial circuit is needed.
Consider a typical installation.
1. All equipment is fed from the same main panel.
2. All equipment has an EGC connected to its chassis.
3. All EGCs originate from the main panel.
4. All RS communication components reference to their equipment chassis.
5. Computer is in an office.
6. A CNC machine is on the shop floor.
7. For simplicity assume both are powered from 120 V. A higher voltage at the CNC just makes the problem worse.
8. Computer to CNC RSxxx communication cable is Belden 8723, but doesn't really matter.
9. At the CNC the hot 120 V line is shorted to the EGC. Note the EGC is the same size and kind of wire as the AC hot. In past times the EGC was smaller, but that even makes the problem worse.
10. Upon occurance of the short from hot to EGC the difference in voltage between the two pieces of equipment is about 1/2 the supply voltage at the shorting end.
11. For a 120 V or higher system this voltage will destroy RSxxx components, and possibly further into the equipment.
You can draw the circuit and study why. Below are scope waveforms that display a real world experiment.
Test setup:
1. Residential 50 kVA pole transformer.
2. 200 A Sq-D main panel.
3. 15 A QO breaker.
4. 50 ft roll of #14 Romex.
5. 25 A 50 mV Weston shunt, 50 A 100 mV. Connected in neutral path.
6. Rigol scope isolated from AC and EGC via Sola constant voltage transformer.
White and black are used. In other words white is being used as the EGC. White and black shorted at the far end. The actual EGC is floated. When the Romex was uncoiled an extension cord was used for extension of the voltage measuring test lead. Uncoiing the Romex produced no great effect.
Blue is voltage and red is current.
Turn on of the short is a random function.
*****
Romex in its original rolled state. Peak voltage slightly over 60 V, and peak current is slightly less than 500 A. Calculated peak current is slightly higher based on 2.5 ohms per 1000 ft. In the third plot you can see the voltage across the white and black wires in series, about 130 V.
.
.
*****
The Romex rolled out moderately straight. Extension cord used to extend voltage probe. Have not incestigated why peak voltage appears lower. The current looks like the same peak. Thus, uncoiling made no difference in current.
.
*****
This plot is the same as the 2nd plot except that the voltage is the source to the breaker, and the voltage scale has been changed. During the short the voltage measured includes voltage drop across the breaker. Looks like the main panel sees about a 50 V drop in the peak at 500 A peak load.
.
.
The purpose of this comment is to show why electrical isolation should be used in an RS232, 422, or 485 communication path. If not isolation, then a sacrificial circuit is needed.
Consider a typical installation.
1. All equipment is fed from the same main panel.
2. All equipment has an EGC connected to its chassis.
3. All EGCs originate from the main panel.
4. All RS communication components reference to their equipment chassis.
5. Computer is in an office.
6. A CNC machine is on the shop floor.
7. For simplicity assume both are powered from 120 V. A higher voltage at the CNC just makes the problem worse.
8. Computer to CNC RSxxx communication cable is Belden 8723, but doesn't really matter.
9. At the CNC the hot 120 V line is shorted to the EGC. Note the EGC is the same size and kind of wire as the AC hot. In past times the EGC was smaller, but that even makes the problem worse.
10. Upon occurance of the short from hot to EGC the difference in voltage between the two pieces of equipment is about 1/2 the supply voltage at the shorting end.
11. For a 120 V or higher system this voltage will destroy RSxxx components, and possibly further into the equipment.
You can draw the circuit and study why. Below are scope waveforms that display a real world experiment.
Test setup:
1. Residential 50 kVA pole transformer.
2. 200 A Sq-D main panel.
3. 15 A QO breaker.
4. 50 ft roll of #14 Romex.
5. 25 A 50 mV Weston shunt, 50 A 100 mV. Connected in neutral path.
6. Rigol scope isolated from AC and EGC via Sola constant voltage transformer.
White and black are used. In other words white is being used as the EGC. White and black shorted at the far end. The actual EGC is floated. When the Romex was uncoiled an extension cord was used for extension of the voltage measuring test lead. Uncoiing the Romex produced no great effect.
Blue is voltage and red is current.
Turn on of the short is a random function.
*****
Romex in its original rolled state. Peak voltage slightly over 60 V, and peak current is slightly less than 500 A. Calculated peak current is slightly higher based on 2.5 ohms per 1000 ft. In the third plot you can see the voltage across the white and black wires in series, about 130 V.
.
.
*****
The Romex rolled out moderately straight. Extension cord used to extend voltage probe. Have not incestigated why peak voltage appears lower. The current looks like the same peak. Thus, uncoiling made no difference in current.
.
*****
This plot is the same as the 2nd plot except that the voltage is the source to the breaker, and the voltage scale has been changed. During the short the voltage measured includes voltage drop across the breaker. Looks like the main panel sees about a 50 V drop in the peak at 500 A peak load.
.
.