Hello, esteemed forum members.
Whilst designing a panel for a 480/277 (Wye) feed, I have approximately 30 amps load of devices which require 230 VAC single phase to operate, so a phase-neutral buck transformer seems like the proper solution. With this drawn out on paper, I have proceeded to the short circuit current rating (SCCR) evaluation of the panel. Can anyone here tell me what effect on the SCCR of secondary-side devices the buck transformer has, if any? In its buck configuration, the transformer has an 8.6 kVA rating.
If I were using an isolation transformer, then I suppose I would not have to worry about devices on the secondary side since the secondary side available fault current is easily calculated from the rated kVA and the secondary voltage. (Please correct me if I err in this last statement.)
With an autotransformer, however, it seems to me that my secondary is not quite so isolated, particularly not so in a short circuit fault.
Does any part of the code address this scenario? If not, should I, for SCCR evaluation purposes, treat the devices on the secondary side of the buck transformer as if they were simply items on a normal (not transformed) branch?
Best regards,
The Shackled Designer
Whilst designing a panel for a 480/277 (Wye) feed, I have approximately 30 amps load of devices which require 230 VAC single phase to operate, so a phase-neutral buck transformer seems like the proper solution. With this drawn out on paper, I have proceeded to the short circuit current rating (SCCR) evaluation of the panel. Can anyone here tell me what effect on the SCCR of secondary-side devices the buck transformer has, if any? In its buck configuration, the transformer has an 8.6 kVA rating.
If I were using an isolation transformer, then I suppose I would not have to worry about devices on the secondary side since the secondary side available fault current is easily calculated from the rated kVA and the secondary voltage. (Please correct me if I err in this last statement.)
With an autotransformer, however, it seems to me that my secondary is not quite so isolated, particularly not so in a short circuit fault.
Does any part of the code address this scenario? If not, should I, for SCCR evaluation purposes, treat the devices on the secondary side of the buck transformer as if they were simply items on a normal (not transformed) branch?