How does running a variable speed drive at more than 60hz effect the wires and motor?
I am wondering about this because a rendering plant I sometimes work at has a lot of problems with 12 awg thhn going bad, then having to pull new wires to fix the problem. they are using inverter rated motors. Just wondering how running the vsd at 90 to 120 hertz will effect the motor and wires.
Shorter runs - higher dv/dt.A critical factor in possible insulation damage is just how fast the drive pulse edges are. To increase efficiency and reduce the stress on the drive transistors, the VFD will try to make the switching transition as fast as possible. But that is also what causes the largest reflections and the greatest insulation damage.
The problem will, I believe, be worse for longer runs of wire.
If you have mostly or entirely short runs or older VFDs with slower transitions, you may have avoided the potential problems. Lower motor voltages relative to the insulation voltage will also minimize the problems.
Tapatalk!
This is the general rule even for 60Hz max operation, keep the runs short, 480 volt operation will have higher peak voltage than 208 or 240 volt and may push the insulation limits of either conductors or the motor itself - especially if not a motor rated for use with a VFD, and the use of line reactors will smooth out the wave some.A critical factor in possible insulation damage is just how fast the drive pulse edges are. To increase efficiency and reduce the stress on the drive transistors, the VFD will try to make the switching transition as fast as possible. But that is also what causes the largest reflections and the greatest insulation damage.
The problem will, I believe, be worse for longer runs of wire.
If you have mostly or entirely short runs or older VFDs with slower transitions, you may have avoided the potential problems. Lower motor voltages relative to the insulation voltage will also minimize the problems.
Tapatalk!
Hookup wire inside of a cabinet is usually so short as to be somewhat irrelevant and you will not likely see insulation damage there. But are you running output wires inside the cabinet to something else besides the motor? If its just the short wires from the VFD terminals to a load reactor or a field wiring TB, I wouldn't get too excited about it.I haven't seen any evidence of failures of this type where I work. A lot of the VFD cabling is SO in the field and THHN in the panels. We have used
VFD cable on our more recent installations but still have THHN in the control panels. Some of these systems have been around for several years and seem ok. We have
one system built by another company that uses line reactors both on the line and load side of all VFD's. Then the cabling to the motors is just SO cable. I do believe everything
I have read about the subject as far as noise and spikes, discharging etc. But how bad is it really? Some of this might be pure marketing.
What would be a better choice for hookup wire in the cabinets?
Yes. I have posted on this before. Here (UK) almost all power cables used in industry are SWAPVC armoured XLPE.All of the "VFD cable" mfrs I have looked at are using XLP, most are rated at 1000V, and of course they all include shielding.
As others have pointed out, provided the motor is operating within it's current rating and is mechanically suitable for the 90/120Hz operation, that ought not to be an issue.I am wondering about this because a rendering plant I sometimes work at has a lot of problems with 12 awg thhn going bad, then having to pull new wires to fix the problem. they are using inverter rated motors. Just wondering how running the vsd at 90 to 120 hertz will effect the motor and wires.
I would love to take credit for that, but it was junkhound that went into that level of detail.Re: GoldDiggers mention of voids in the PVC insulation of THHN, he his dead on. It may be fine for a while, but most responsible VFD mfrs are telling people to NOT use THHN if it can be avoided and use XLP insulated wire instead. All of the "VFD cable" mfrs I have looked at are using XLP, most are rated at 1000V, and of course they all include shielding.
How does running a variable speed drive at more than 60hz effect the wires and motor?
If you count the OP's first two posts (before any answers were given), then the replies are pretty relevant:hee hee.. all the replies so far are generic and are applicable at ANY FREQUENCY: none have answered the OP question.....
So to the OP ACTUAL question: not at all, other than motor goes faster.....
And the answer to that is that running the VFD at 90 to 100Hz will not affect the wires any more than running the same VFD and motor at 60Hz or less as long as the voltage is not raised above the nominal voltage when the VFD goes to higher than nominal speeds.I am wondering about this because a rendering plant I sometimes work at has a lot of problems with 12 awg thhn going bad, then having to pull new wires to fix the problem. they are using inverter rated motors. Just wondering how running the vsd at 90 to 120 hertz will effect the motor and wires.
hee hee.. all the replies so far are generic and are applicable at ANY FREQUENCY: none have answered the OP question.....
So to the OP ACTUAL question: not at all, other than motor goes faster.....
As others have pointed out, provided the motor is operating within it's current rating and is mechanically suitable for the 90/120Hz operation, that ought not to be an issue.
I keep reading about this issue, but the plant I often work at has a couple of hundred VFDs all installed using THWN, with a lengths well over 100'...it often takes over 75' of wire just to get out of the MCC room. We don't have any of those issues. These are all 3 phase 480 volt motors from 1/2 to 500 hp.
The only drives we have used 1,000 volt rated wire on are the large DC drives, but the armature voltage on those is 700 volts, so we can't use 600 volt rated wire.
Or similar.In many neon advertisement boards people use ordinary house wires to supply neon lamps from transformer MV output. The installation works for some time. It is because dielectric breakdown is a statistical process. Out of large number neon advertisement boards with household wires, some may continue to operate indefinitely without any breakdown.
Perhaps the same mechanism at work in Don's case?