Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
When installing a raceway as an EGC.Do you just assume it meets 250.122(A) and subsequently 250.4A)(5)? Or is there test that have to be done?
How do we know that our raceway is "capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source."??
Like if I have a 100 amp circuit I need a #8 CU EGC... Can I just assume that whatever raceway size is needed to meet fill can handle that amount of current to clear a fault???
How do we know that our raceway is "capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source."??
Like if I have a 100 amp circuit I need a #8 CU EGC... Can I just assume that whatever raceway size is needed to meet fill can handle that amount of current to clear a fault???