Effectively Grounded

Status
Not open for further replies.
How is Effectively Grounded different from solidly grounded?

What is zero sequence reactance? What is zero sequence, positive sequence and negative sequence anyway?

Have a great day to all
 
Re: Effectively Grounded

To me, the term "effective" sounds like a performance function whereas the term "solidly" sounds like a mechanical function.
 
Re: Effectively Grounded

Effectively Grounded: Grounded through a sufficiently low impedance such that for all system conditions the ratio of zero sequence reactance to positive sequence reactance (Xo/Xl) is positive and less than 3, and the ratio of zero sequence resistance to positive-sequence reactance (R0/Xl) is positive and less than 1.

Solidly Grounded: Connected directly through an adequate connection in which no impedance has been intentionally added. Typically used to describe a single or poly-phase grounded system, whereas you could have a resistive or impedance grounded transformer.
 
Re: Effectively Grounded

I have seen this term used in engineering specs. Usually it refers to how an individual device is bonded to the EGC.

For instance, a common statement I used to see was something along the lines of "devices with sheet metal enclosures mounted in the the face of the enclosure using screws to hold the device in place are considered effectively grounded, and do not require a seperate grounding conductor". I was never sure why they would make such a statement in the first place. It does not seem like a big cost savings, so why?

I generally ignored such prononcements on the theory that if there is a ground terminal on the device it ought to have a green wire connected to it.
 
Re: Effectively Grounded

Originally posted by poweringtech: What is zero sequence? positive sequence? and negative sequence? How are reactances determined?
What are they? They are the first half of a semester-long course on electrical analysis. There is no easy way to explain the concepts in this type of Forum discussion. But here is a very quick, simplistic introduction:

We all know that we are supposed to balance the loads on each service, switchboard, panel, whatever. Some of us are aware that in a balanced three phase system, the true power is constant (i.e., does not vary form moment to moment). But what happens when the load is not balanced? Also, what happens when there is an unbalanced fault (e.g., single-line-to-ground)?

Some brilliant guy (whose name I could look up, but you all can use Google too) submitted a short mathematical paper (that led to his being awarded a PhD) that proved that any unbalanced system can be modeled with a set of three balanced systems. Instead of the original (unbalanced) Phases A, B, and C, you use the three sets (A1, B1, C1), and (A2, B2, C2), and A0, B0, C0). Each of the three new sets is balanced by itself. The class you take to learn about this stuff tells you how to calculate the values of the three sets, and how to use them to analyze the original (unbalanced) system.

The first set, called the ?Positive Sequence,? rotates in the same pattern as the original set. That is, the sequence of the original is A, then B, then C. The sequence of the new set is A1, then B1, then C1.

The second set, called the ?Negative Sequence,? rotates in the opposite pattern as the original set. That is, the sequence of the original is A, then B, then C. The sequence of the new set is A2, then C2, then B2.

The third set, called the ?Zero Sequence,? does not rotate at all. That is, while the original Phase A voltage is out of phase from the original Phase B voltage by 120 degrees, the three ?Zero Sequence Voltages? VA0, VB0, and VC0 are in phase with each other. It should be noted that the fact that these are in phase is a key reason that the 3rd order harmonic currents add in the neutral, and a key reason for sometimes having to use a 200% neutral conductor.
 
Re: Effectively Grounded

The man was Charles (I believe) Fortescue (sp?). He was with Westinghouse. The classical work developing the technique was done by Edith Clarke, at General Electric.
Do your Google search on ?Symmetrical Components.?

[ April 18, 2005, 12:41 PM: Message edited by: rbalex ]
 
Re: Effectively Grounded

Thank you very much for your reply. Any book that you can recommend or if you have pdf file about this topic I will surely appreciate.

Have a great day to all. God bless you all always
 
Re: Effectively Grounded

In a given system how is zero sequence reactance determined. How about positive sequence and negative sequence reactance? where can we get this value?

Thanks,
Bob
 