Hello Everyone,
I have a situation where the customer owns the medium voltage equipment (switchgear) and feeds a number of transformers (12.47KV-480Y/277V). I know we don't pull EG for utility transformers to the main switchboard (first disconnecting means). Since this transformer is not owned by the utility, is EG still required to be pulled in addition to the phase and neutral conductors? If not, can the grounded conductor (neutral) be sized based on table 250.66?
Thanks,
I have a situation where the customer owns the medium voltage equipment (switchgear) and feeds a number of transformers (12.47KV-480Y/277V). I know we don't pull EG for utility transformers to the main switchboard (first disconnecting means). Since this transformer is not owned by the utility, is EG still required to be pulled in addition to the phase and neutral conductors? If not, can the grounded conductor (neutral) be sized based on table 250.66?