Thanks. Could they actually ask for a separate EGC be pulled in common conduit for each circuit. Which code section references needing to only include one EGC in a "homerun" pipe? THanksCorrect - EGC sized to largest OCPD protecting any conductor in the conduit, or at least no larger than the associated ungrounded conductor in some cases. Motor circuits is where this can be common - say you have a 45 amp breaker but 12 AWG motor conductors (can happen) - the EGC need not be larger than the 12 AWG ungrounded conductors in that case.
That is a design issue. If the project specifications call for an EGC for each circuit, you need to install it, unless you took exception to that when the bid was submitted.Thanks. Could they actually ask for a separate EGC be pulled in common conduit for each circuit. Which code section references needing to only include one EGC in a "homerun" pipe? THanks
250.122 (C) Multiple Circuits.
A single equipment grounding conductor shall be permitted to be installed for multiple circuits that are installed in the same raceway, cable, trench, or cable tray. It shall be sized from Table 250.122 for the largest overcurrent device protecting circuit conductors in the raceway, cable, trench, or cable tray. Equipment grounding conductors installed in cable trays shall meet the minimum requirements of 392.10(B)(1)(c).
Sure, they could over design and waste lots of money in the process for zero added safety.Thanks. Could they actually ask for a separate EGC be pulled in common conduit for each circuit. Which code section references needing to only include one EGC in a "homerun" pipe? THanks
Those EGC's do count as conductor fill and could require you to increase raceway size because of more fill.Sure, they could over design and waste lots of money in the process for zero added safety.