I am looking for guidance in as far as the Grounding Conductor sizing when installed along with PH Cnductors that are tapped conductors AND per 240.12(b)(5) considered outside of building.
The TAP conductors (CU) which are are rated at 380A.
The TAPPED conductors are rated at 175A @ 75c
Am i correct in assuming that since there must be an OCD for this feeder once it enters the building that the EG sizing would be per the OCD in this
device / disconnect?
The TAP conductors (CU) which are are rated at 380A.
The TAPPED conductors are rated at 175A @ 75c
Am i correct in assuming that since there must be an OCD for this feeder once it enters the building that the EG sizing would be per the OCD in this
device / disconnect?