ptonsparky
Tom
- Occupation
- EC - retired
Recently installed a VFD for a submersible pump. While removing the old pump panel I noticed a transfer switch had been installed ahead of it. (Two sevices to the facility plus a generator will allow for pump operation from any one of three sources.) Checking things out I found that the standby side was energized, two of three phases were good, third had no voltage. No EG was installed with those conductors. Direct bury about 500. While the equipment is bonded via the grounded conductor from the normal service I believe that the standby side requires an EG installed with those conductors and informed the owner this needs to be corrected. He is not happy with the EC that installed it.
250.134(B) is my basis, any others?
250.134(B) is my basis, any others?