stew
Senior Member
- Location
- federal way,washington
Heres the scenario. A 600 amp service feeding 3 service disconnects mounted below the ct can. 2 have 200 amp breakers with 4/0 al feeders and 1 has 225 amp breaker with 250 mcm feeders.
These go out to a line of quad out let boxes with feed thru lugs. The setup is 4 quads on one,four quads on 2 and 5 quads on 3. The egc I have chosen is #2al use. Is it permissible to bond all the cans together and run 1 egc out to the loads or do I need an individual egc for each panel? All the feeders are use and will be buried with no conduit at 24 inches.
[ June 09, 2004, 11:57 PM: Message edited by: stew ]
These go out to a line of quad out let boxes with feed thru lugs. The setup is 4 quads on one,four quads on 2 and 5 quads on 3. The egc I have chosen is #2al use. Is it permissible to bond all the cans together and run 1 egc out to the loads or do I need an individual egc for each panel? All the feeders are use and will be buried with no conduit at 24 inches.