C cppoly Senior Member Location New York Jan 18, 2013 #1 Is a conductor with green insulation along its entire length allowed to be used as a neutral conductor if it is taped on both ends with white or gray? Both cases: smaller and larger than 6 AWG.
Is a conductor with green insulation along its entire length allowed to be used as a neutral conductor if it is taped on both ends with white or gray? Both cases: smaller and larger than 6 AWG.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 18, 2013 #2 No. See 250.119. 250.119 ... Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors. Click to expand...
No. See 250.119. 250.119 ... Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors. Click to expand...
C cppoly Senior Member Location New York Jan 18, 2013 #3 don_resqcapt19 said: No. See 250.119. Click to expand... Thanks. I was looking in Article 200 identification section, but couldn't find it there.
don_resqcapt19 said: No. See 250.119. Click to expand... Thanks. I was looking in Article 200 identification section, but couldn't find it there.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 18, 2013 #4 Oh, the horror...........silly rule IMPO.