One EGC can serve both voltage systems. There is no code requirement for separate EGC's. If a wire EGC is not run, then the metal raceway, assuming it's listed in 250.118, is suitable.
2005 NEC 300.3(c)(1)----conductors of different sysytems can occupy the same raceway,cable,enclosure if the insulation voltage rating is not less than the maximum circuit voltage.