EGC--Different systems in same conduit.

Status
Not open for further replies.
One EGC can serve both voltage systems. There is no code requirement for separate EGC's. If a wire EGC is not run, then the metal raceway, assuming it's listed in 250.118, is suitable.
 
The insulation value have to be the same Value to 600 V.
In respects to mixed service sizes.

Sorry not at the Code Book...
 