Quick Question!
Article 314.16 (b)(5) 2020 NEC states that where up to four EGC enter a box , that a single volume allowance in accordance with Table 314.16(B) shall be made based on the largest conductor.
I am confused about something. Lets say I have 5 - # 14 AWG CU EGC and 5 - #12 AWG CU. EGC. When doing the calculation do I just forget about the # 14AWG conductors or do I add them to the number 12AWG, so instead of having 5 # 12 AWG CU I would have 10 # 12 AWG.
Article 314.16 (b)(5) 2020 NEC states that where up to four EGC enter a box , that a single volume allowance in accordance with Table 314.16(B) shall be made based on the largest conductor.
I am confused about something. Lets say I have 5 - # 14 AWG CU EGC and 5 - #12 AWG CU. EGC. When doing the calculation do I just forget about the # 14AWG conductors or do I add them to the number 12AWG, so instead of having 5 # 12 AWG CU I would have 10 # 12 AWG.