Is the grounding terminals in switch boxes and in the A/C units' cabinet rated for 90? termination ?
Example(s); Two side by side A/C units, one has a MCA of 18.9 and a Maximum OCPD of 30 Amps.
This would allow 14 AWG for circuit and EGC.
The other A/C unit has a MCA of 21.6 and a Maximun OCPD of 30 Amps.
This would allow 12 AWG for circuit conductors, but if the Grounding terminals are rated for 90? then would a 14AWG egc be permitted ?
Example(s); Two side by side A/C units, one has a MCA of 18.9 and a Maximum OCPD of 30 Amps.
This would allow 14 AWG for circuit and EGC.
The other A/C unit has a MCA of 21.6 and a Maximun OCPD of 30 Amps.
This would allow 12 AWG for circuit conductors, but if the Grounding terminals are rated for 90? then would a 14AWG egc be permitted ?