Questions on running an EGC to Ungrounded receptacles. Please correct me if I make any erroneous assumptions leading up to my question and forgive any improper use of terms. This is residential btw, NYS, Nassau County.
To my knowledge, 250.130(C) allows for a separate EGC to be run from the grounding bus bar in the main panel to a receptacle to provide an EGC for an ungrounded receptacle, allowing you to replace that receptacle with a grounding type receptacle.
My question:
From there, if I wanted to run an EGC to any other currently ungrounded receptacles on the same circuit, would I also have to run each EGC back to the main panel because of 250.130(C)(5)? Or would I be able to run an EGC from the circuit to a junction box and then run individual conductors to each receptacle?
For the time being, let's forget the fact that if I'm fishing wire I might as well just run a new NM-B WG from the panel anyway.
To my knowledge, 250.130(C) allows for a separate EGC to be run from the grounding bus bar in the main panel to a receptacle to provide an EGC for an ungrounded receptacle, allowing you to replace that receptacle with a grounding type receptacle.
My question:
From there, if I wanted to run an EGC to any other currently ungrounded receptacles on the same circuit, would I also have to run each EGC back to the main panel because of 250.130(C)(5)? Or would I be able to run an EGC from the circuit to a junction box and then run individual conductors to each receptacle?