If you ran it in metal conduit or EMT, you can just skip the wire type EGC entirely.I have 60A, 208V feeder to feed 60A 102/208V panel.
Due to the length, I upsized the conductor to 4#4AWG + 10G. I realized I didn’t upsize the EGC. Will I be ok with this?
Thank you.
Is that a codified local or state amendment?If the inspector will allow the conduit to be the EGC, around here they require a wire type EGC to be ran regardless.
If the inspector will allow the conduit to be the EGC, around here they require a wire type EGC to be ran regardless.
If you use a wire type egc I think you need to upsize to #8 because when increasing from 6awg (26,240 cm) to 4awg (41,740 cm) that's an increase of 1.59I have 60A, 208V feeder to feed 60A 102/208V panel.
Due to the length, I upsized the conductor to 4#4AWG + 10G. I realized I didn’t upsize the EGC. Will I be ok with this?
Thank you.
I agree that is what the code requires, but when you run the numbers you will find that the 4AWG with the 10 AWG EGC will flow slightly more fault current than the 6 AWG with the 10 AWG EGC. This assumes the same circuit length in both cases.If you use a wire type egc I think you need to upsize to #8 because when increasing from 6awg (26,240 cm) to 4awg (41,740 cm) that's an increase of 1.59
10awg has a cm of 10,380 which when multiplied by 1.59 = 16,504.2 cm
8awg is 16,510 cm
I would install an 8awg egc
some might say that you don't have to go with 8awg until 100 amps per Table 250.122 but I'm just looking at the rule ad it's written and erring on the side of caution that is in keeping with 250.4(A)(5)
Of course. But won't that translate to the #10 having a greater share of the total voltage drop?I agree that is what the code requires, but when you run the numbers you will find that the 4AWG with the 10 AWG EGC will flow slightly more fault current than the 6 AWG with the 10 AWG EGC. This assumes the same circuit length in both cases.
Right, but they do have the authority to make life hell or like roses.The inspector has no authority to make rules.
In other words, the code section makes very little sense. The assumption is that wires will only be upsized for voltage drop over very long wire runs. And yet if the wire is very long but not sized to account for voltage drop, the code section doesn't kick in, even though the danger it putatively addresses is greater.I agree that is what the code requires, but when you run the numbers you will find that the 4AWG with the 10 AWG EGC will flow slightly more fault current than the 6 AWG with the 10 AWG EGC. This assumes the same circuit length in both cases.
So what?Of course. But won't that translate to the #10 having a greater share of the total voltage drop?
which there exists a standard for>Consider that the egc doesn't do anything UNTIL it needs to and then you want it to open the OCPD as fast as possible
The current flow operates the OCPD and voltage drop does not really matter.Of course. But won't that translate to the #10 having a greater share of the total voltage drop?
Well yes and no, the voltage drop would reduce the fault current, increasing the time for the ocp to trip. I’ve had that happen on long parking lot runs. Does it matter? Depends on the situation. Tends to destroy the breakers quicker because the fault current on the contacts though lower, is not cleared as fast.The current flow operates the OCPD and voltage drop does not really matter
along with anything else in it's path......Tends to destroy the breakers quicker because the fault current on the contacts though lower, is not cleared as fast.
In theory I agree, but in practice it happens all the time.The inspector has no authority to make rules.