Greetings. This is my first post to the forum; I've been very impressed by the general level of knowledge and professionalism here compared to other forums. I truly believe that folks here are trying to help others.
I'm in the process of installing several conduits between a motor controller and a pump unit. Looking to verify if either NEC (or individual's) recommendations indicates a need for an Equipment Grounding Conductor in Conduits "A", "B", and "C" (or other changes) under the following conditions:
1. Power to a motor controller is supplied via one branch circuit. All voltages used by the controller (and equipment external to the controller) are derived within the controller.
2. Conduit "A" contains all six motor conductors and the only EGC. The motor is driven by a Wye-Delta starter in the controller. This conduit includes a 3' section of greenfield at the controller end and 3' of non-metallic flex at the pump end, with EMT between. Voltages are between 208VAC and 600VAC. EGC is connected at controller and at motor/pump, and is sized same as the individual motor conductors.
3. Conduit "B" contains several pairs of 18AWG conductors used to operate solenoid valves. All voltages are 120VAC; load on any given pair will not exceed 1.2A. Conduit setup is similar to Conduit "A" except smaller. Presently no EGC is proposed to be installed in Conduit "B".
4. Conduit "C" contains a multiconductor cable (24AWG x 8) that carries signals up to 24Vdc at <10mA. Conduit "C" is comprised of FMC (Greenfield) from motor/pump unit to the controller. No additional EGC is installed in Conduit "C".
5. Grounding Bushings are installed inside controller for Conduit "A" and "B".
The configuration is intended to address potential EMC issues. Have I overlooked anything (especially regarding NEC Article 250)? Any recommendations or or comments from the experts? And especially important, why?
Thanks in advance,
Jeff
I'm in the process of installing several conduits between a motor controller and a pump unit. Looking to verify if either NEC (or individual's) recommendations indicates a need for an Equipment Grounding Conductor in Conduits "A", "B", and "C" (or other changes) under the following conditions:
1. Power to a motor controller is supplied via one branch circuit. All voltages used by the controller (and equipment external to the controller) are derived within the controller.
2. Conduit "A" contains all six motor conductors and the only EGC. The motor is driven by a Wye-Delta starter in the controller. This conduit includes a 3' section of greenfield at the controller end and 3' of non-metallic flex at the pump end, with EMT between. Voltages are between 208VAC and 600VAC. EGC is connected at controller and at motor/pump, and is sized same as the individual motor conductors.
3. Conduit "B" contains several pairs of 18AWG conductors used to operate solenoid valves. All voltages are 120VAC; load on any given pair will not exceed 1.2A. Conduit setup is similar to Conduit "A" except smaller. Presently no EGC is proposed to be installed in Conduit "B".
4. Conduit "C" contains a multiconductor cable (24AWG x 8) that carries signals up to 24Vdc at <10mA. Conduit "C" is comprised of FMC (Greenfield) from motor/pump unit to the controller. No additional EGC is installed in Conduit "C".
5. Grounding Bushings are installed inside controller for Conduit "A" and "B".
The configuration is intended to address potential EMC issues. Have I overlooked anything (especially regarding NEC Article 250)? Any recommendations or or comments from the experts? And especially important, why?
Thanks in advance,
Jeff